    Section 24
    Blasting Operations
    This section discusses blasting operations, with specific focus on the following

    areas:

    • General Requirements
    • Radio and Electromagnetic Radiation
    • Transporting Explosives
    • Transporting Explosives Underground
    • Storing Explosives
    • Handling Explosives
    • Loading Explosives and Blasting Agents
    • Wiring operations
    • Firing explosives
    • Inspection following a blast
    • Misfires
    • Using safety fuses
    • Using detonator cord
    • Underwater blasting
    24.1 General Requirements for Blasting Operations
    In addition to the requirements of this section, the transportation, handling,
    storage, and use of explosives are subject to provisions of ANSI A10.7 - Safety
    Requirements for Transportation, Storage, Handling, and Use of Commercial
    Explosives and Blasting Agents; 29 CFR 1910.109 - Explosives and Blasting
    Agents; 29 CFR 1926, Subpart U - Blasting and the Use of Explosives (1926.900
    to 1926.914); and 27 CFR Part 55 - Commerce in Explosives.
    24.1.1 Competent Supervision. A blasting supervisor must be designated to
    direct and supervise all blasting operations. This includes the transportation,
    handling, storage, and use of explosives and blasting agents. The supervisor must
    provide written records of past experience to the employer as evidence of
    competency.
    24.1.2 Qualifications.
    a. Personnel. Employees who transport, store, handle, or use explosives
    or blasting agents must be at least 21 years of age. They must be able to
    give and understand written and verbal instructions.
    Reclamation Safety and
    Health Standards
    24-2 October 2009
    b. Blasters. Blasters must be qualified through training, knowledge, and
    experience in transporting, storing, handling, and using explosives, and
    have a working knowledge of State and local laws and regulations which
    pertain to explosives. Blasters must hold a Federal, State, or local license
    or certificate, have proof of formal training attended within the last
    5 years, or three recommendations from past employers or explosives
    manufacturers testifying to the blaster’s knowledge and ability to perform
    in a safe manner the type of blasting that will be required.
    24.1.3 Blasting Plan. Submit a comprehensive blasting plan before the start of
    blasting operations and have it approved. The blasting plan may be submitted as
    part of the overall site safety plan, as required by the "Contractor Requirements"
    section of these standards (for contract operations) or as a supplementary plan to a
    Job Hazard Analysis. Explosives must not be transported onto the jobsite before
    the plan has been approved. The plan must identify proposed methods and
    procedures for conforming with referenced standards and regulations, and it must
    include the following information:
    • Method and equipment for transporting explosives and detonators
    • Type and location of storage facilities
    • Type and quantity of explosives and detonators
    • Primer assembly procedure and location
    • Employee training programs
    • Provisions for protecting people, structures, and private and public
    property
    • Provisions for developing and distributing a daily blasting plan
    covering hole diameter, spacing, loading, and delay patterns
    • Provisions for disposal of explosives, blasting agents, and associated
    materials
    24.1.4 Security and Inventory. Secure and protect explosives from theft.
    Maintain an accurate running inventory of all explosives stored at the jobsite.
    Such records must be available. Promptly report any loss or theft to the
    appropriate authorities.
    24.1.5 Notifications. Notify the owners and operators of the facility and take all
    necessary precautions for the safe control of the blasting operations before
    beginning blasting operations in the immediate vicinity of buildings, public roads,
    overhead powerlines, utility services, or similar facilities. At least 24 hours
    before blasting in the vicinity of gas, electric, water, communications, or other
    utilities is to begin, the blasting supervisor must notify appropriate utility
    representatives.
    Section 24—Blasting Operations
    October 2009 24-3
    24.1.6 Smoking Restrictions. Prohibit smoking, firearms, matches, open flame
    lamps, fire, heat-producing devices, and sparks in or near explosive storage sites
    or in areas where explosives are handled, transported, or used.
    24.1.7 Thunderstorms. Discontinue the handling or use of explosives during
    the approach and progress of a thunderstorm. All employees must leave the
    danger areas and seek a place of safety when these conditions are present. Install
    an approved lightning warning device capable of detecting atmospheric
    conditions that could produce lightning on the jobsite. Warning devices must be
    acceptable to the COR or office head before installation.
    24.1.8 Damage Control. Take precautions to minimize ground vibration,
    airblast, and flyrock. Include a damage control section in the site blasting plan
    that addresses these issues. Use blasting mats where flyrock damage is possible.
    Use modern blasting seismographs and methods to measure ground vibrations and
    air blast levels at designated structures or locations. Unless otherwise specified,
    control the blasting so that ground vibrations and airblast levels do not exceed the
    following:
    Ground Vibration Limits1
    Type of Structure2
    Peak Particle Velocity (inches per second)
    At Low Frequency3
    (<40 Hertz)
    At High Frequency
    (>40 Hertz)
    Modern homes, drywall
    interiors 0.75 2.0
    Older homes, plaster on
    wood lath construction for
    interior walls
    0.5 2.0
    Reference: Siskind, D.E., M.S. Stagg, J.W. Kopp, and C.H. Dowding, “Structure Response and
    Damage Produced by Ground Vibration from Surface Mine Blasting.” U.S. Department of the
    Interior, Bureau of Mines, Report of Investigations RI 8507, 1980.
    1The graph in Appendix B of the above reference may be used in lieu of the limits listed in this
    table.
    2For precarious structures not listed in the table, use the limits for older homes; for all other
    structures not listed in the table, use the limits listed for modern homes.
    3All spectral peaks within 50 percent amplitude of the predominant frequency must be analyzed.
    Airblast Limits
    Instrumentation Air Blast (decibels)
    0.1 hertz high-pass system 134
    2 hertz high-pass system 133
    5 or 6 hertz high-pass system 129
    C-slow (for events not exceeding 2 seconds’ duration) 105
    Reference: Siskind, D.E., V.J. Stachura, M.S. Stagg, and J.W. Kopp, “Structure Response
    and Damage Produced by Airblast from Surface Mining,” U.S. Department of the Interior, Bureau of
    Mines, Report of Investigations RI 8485, 1980.
    Reclamation Safety and
    Health Standards
    24-4 October 2009
    24.1.9 Warning Signs. Post warning signs at access points to blasting areas.
    24.1.10 Destruction of Explosives. Deteriorated or damaged explosives,
    blasting agents, blasting supplies are prohibited. Destroy and remove these and
    all excess explosives from the site in accordance with the specific written
    instructions of the manufacturer.
    24.1.11 Empty Explosive Containers. Destroy empty boxes and combustible
    packing materials which have contained explosives in accordance with the
    manufacturer’s disposal procedures. If disposal is through burning, all personnel
    must remain at least 100 feet from the burning site once the material has been
    ignited and until no visible flames or smoke have been detected for 1 hour.
    24.1.12 Fire. If a fire begins that involves explosives, or where the danger of the
    fire contacting explosives is imminent, do not fight the fire. All personnel must
    seek safe shelter; guard the fire area to prevent intruders.
    24.2 Radio and Electromagnetic Radiation
    Take adequate precautions to prevent accidental discharge of electric blasting
    caps from current induced by radar, radio transmitters, powerlines, and similar
    sources of electromagnetic radiation.
    24.2.1 Mobile Radio Transmitters. Mobile radio transmitters or cellular
    telephones within 100 feet of electric blasting caps or delays not in their original
    containers are prohibited unless de-energized and effectively locked.
    Post warning signs at least 36 by 42 inches in size, stating BLASTING ZONE—
    TURN OFF 2-WAY RADIOS AND CELLULAR TELEPHONES, on all public
    roads within 1,000 feet of blasting operations, using electronic detonators.
    24.2.2 Non-electric Firing Systems. If it is not possible to observe the safe
    clearance distances from radio frequency (RF) transmitter stations, as set forth in
    Institute of Makers of Explosives (IME) publication 20, "Safety Guide for the
    Prevention of Radio Frequency Radiation Hazards in the Use Of Electric Blasting
    Caps," use nonelectric firing systems to blast. Electrical detonators must not be
    stored or used within the IME-specified distances of a transmitter station.
    24.3 Requirements for Transporting Explosives
    Transporting explosives by air, water, or on public highways must comply with
    the provisions of US Department of Transportation Regulations contained in
    46 CFR 146-149 - Water Carriers; 49 CFR 171-177 Subchapter C - Hazardous
    Materials Transportation; and 49 CFR 390-397, "Motor Carriers."
    24.3.1 Vehicles. Vehicles used to transport explosives must conform to the
    following requirements:
    Section 24—Blasting Operations
    October 2009 24-5
    a. They must be in good repair, with all electrical wiring completely
    protected and securely fastened to prevent short circuits.
    b. They must have tight floors. Cover any exposed spark-producing metal
    with wood or other nonsparking material to prevent contact with
    containers of explosives.
    c. Do not load them beyond rated capacity, and secure the explosives to
    prevent shifting or dislodgment.
    d. Transport explosive materials in open-bodied motor vehicles only if
    they have been loaded into a portable magazine that is securely fastened to
    the truck bed. Never transport explosive materials in open-bodied motor
    vehicles that depend on a fire-resistant tarpaulin cover for protection.
    e. Mark vehicles transporting explosives with reflectorized signs on both
    sides and the front and rear with "EXPLOSIVES" in red letters. Make
    letters at least 4 inches high on a white background or placarded in
    accordance with 49 CFR Part 172, Subpart F - "Placarding."
    f. Equip them with two or more fire extinguishers with a rating of at least
    2-A:40-B:C.
    g. Inspect them daily before use to ensure that the vehicle is in proper
    condition for safe transportation. The inspection must determine that fire
    extinguishers are charged and ready; electric wiring is protected and
    fastened to prevent short circuiting; chassis, motor, pan, and underbody
    are reasonably clean and free of oil and grease; fuel tanks and lines are
    secure and have no leaks; tires are in serviceable condition with proper
    inflation; and lights, brakes, horns, wipers, etc., are functioning properly.
    24.3.2 Vehicle Operators. Motor vehicle operators transporting explosives must
    be at least 21 years old and be properly licensed drivers. Drivers must be
    physically fit, careful, capable, and reliable. Drivers must not be unlawful users
    of, or addicted to, alcohol, narcotics, or dangerous drugs. Drivers must be
    familiar with applicable local, State, and Federal laws and regulations governing
    the transportation of explosive materials. Transportation on Federal highways or
    other public roads requires a commercial driver's license.
    24.3.3 Caps and Detonators. Do not transport blasting caps and detonators with
    other explosives unless the blasting caps or detonators are in a closed metal
    storage container that has at least a 2-inch wood lining. Such containers must be
    at least 2 feet away from other explosives.
    24.3.4 Flammable Materials. Do not transport spark-producing tools, carbides,
    oil, matches, firearms, acids, storage batteries, oxidizing or corrosive compounds,
    or flammable materials with explosives.
    Reclamation Safety and
    Health Standards
    24-6 October 2009
    24.3.5 Parking. Attend vehicles containing explosives at all times. Do not park
    loaded vehicles, even if attended, near any bridge, tunnel, or other structure that
    may be occupied or locations where people may congregate or assemble.
    24.3.6 Fueling. Do not refuel vehicles while they are carrying explosives.
    24.3.7 Smoking Restrictions. Employees who transport, handle, or use
    explosives must not smoke or carry on their persons or in the vehicle matches,
    lighters, firearms, ammunition, or flame-producing devices of any description.
    24.3.8 Riders. Permit only the authorized driver and helper to ride on trucks
    transporting explosives or detonators.
    24.4 Requirements for Transporting Explosives Underground
    In addition to the requirements set forth in the previous subsection,
    "Requirements for Transporting Explosives," the provisions of this subsection
    apply to underground transportation of explosives.
    24.4.1 Hoists. Notify the hoist operator before transporting explosives or
    blasting agents in a shaft conveyance. Do not permit any person to ride a hoist or
    shaft conveyance transporting explosives or blasting agents. Do not transport
    detonators while transporting explosives.
    24.4.2 Powder Cars and Trucks. Convey explosives and blasting agents only
    in specifically built or equipped insulated powder cars or truck-mounted
    containers approved by the State entity having jurisdiction. Mark powder cars
    with reflectorized signs on both ends and sides with "EXPLOSIVES" in letters at
    least 4 inches high against a sharply contrasting background at all times that there
    are explosives in the car. Cover or remove the signs when no explosives are
    present. Do not transport explosives or blasting agents on a locomotive; at least
    two car lengths must separate the locomotive from the powder car. Pull (do not
    push) powder cars.
    24.4.3 Common Transport of Detonators and Explosive Materials.
    Physically separate compartments for transporting both detonators and explosive
    materials in the same conveyance or car by at least 24 inches or by a solid
    partition at least 6 inches thick. Do not transport detonators and other explosive
    materials together in any shaft-conveyance.
    24.4.4 Transportation of Personnel and Explosives. No personnel, other than
    the transport operator, helper, and the individuals handling the explosives may
    ride transports carrying explosives.
    24.4.5 Truck Transportation. Trucks transporting explosives underground
    must meet other applicable provisions of these standards and have their electrical
    systems checked weekly to detect possible electrical hazards. A written record of
    Section 24—Blasting Operations
    October 2009 24-7
    such inspections must be maintained. Auxiliary lights on truck beds powered by
    the truck's electrical system are prohibited. Do not store explosives in trucks.
    24.4.6 Transporting Explosives to the Face or the Loading Area. Take only
    the quantity of explosives or blasting agents estimated necessary for the blast to
    the face or loading area. Take explosives or blasting agents to the loading area
    only after the drilling has been completed and the holes are ready to be loaded.
    Remove surplus explosives and blasting agents from the area before wiring up the
    blast.
    24.4.7 Makeups. Make up primers and delays at the face or loading area, unless
    a primer-makeup plan is submitted and approved.
    24.5 Explosives Storage
    24.5.1 Requirement. Store explosives and related materials in approved
    magazines and in accordance with the applicable provisions of the Bureau of
    Alcohol, Tobacco, and Firearms as set forth in 27 CFR 55, "Commerce in
    Explosives." Magazines must be bulletproof, rodent-resistant, weather-resistant,
    ventilated, and constructed to the standards of the Bureau of Alcohol, Tobacco,
    and Firearms, or the Institute of Makers of Explosives.
    24.5.2 Magazine Location. Locate explosives magazines in accordance with the
    State and local laws. The COR or office head must approve the proposed sites
    before location or construction. Consider contractor and Government offices,
    shops, etc., to be inhabited buildings when determining magazine locations,
    quantities, and safe distances.
    24.5.3 Notifications. Notify local authorities, such as law enforcement agencies
    and fire departments, of the type, planned quantity, and storage location on the
    site before bringing explosives onto a site for storage.
    24.5.4 Detonators. Do not store blasting caps, electric blasting caps, detonating
    primers, and primed cartridges in the same magazine as other explosives or
    blasting agents. Locate detonator magazines at least 100 feet from magazines
    containing other explosives or blasting agents, if unbarricaded, and at least 50 feet
    away, if barricaded.
    24.5.5 Combustible Materials. Do not permit smoking or open flame within
    100 feet of storage magazines. Remove vegetation and combustible material
    within 25 feet of all magazines.
    24.5.6 Security. Securely lock magazines at all times except to inspect or move
    explosives. Maintain an inventory of all storage and withdrawal of explosives.
    Inspect magazines storing explosives at least every 7 days to ensure that there has
    been no unauthorized entry or removal of explosives.
    Reclamation Safety and
    Health Standards
    24-8 October 2009
    24.5.7 Posting. Post areas around magazines with "EXPLOSIVES" signs. Place
    the signs so that a bullet passing through the sign will not strike a magazine.
    24.5.8 Storage. Store explosives in their original containers. Store containers of
    explosives with the top side up as designated on the container. Use the oldest
    stock of explosives first.
    24.5.9 Maintenance. Promptly remove debris and combustible material from
    magazines. When magazine floors become stained with explosives, clean them in
    accordance with the explosive manufacturer’s instructions.
    24.5.10 Transfer In and Out. Provide for the safe transfer of explosives in and
    out of magazines, including providing ramps or walkways, as necessary.
    24.5.11 Storage Underground. Do not permanently store explosives
    underground. Temporary storage must comply with the following requirements:
    a. Powder Cars. Restrict temporary storage to limited supplies stored in
    specially designed powder cars located at least 1,000 feet from the face or
    blasting area. Do not permit transformers, storage of flammable materials,
    welding, open flame, smoking, and other ignition sources within 100 feet
    of the powder car.
    b. Posting and Lighting. Designate the storage area or siding by a red
    light visible in all directions, and post both ends of the powder car with a
    luminous sign, stating "EXPLOSIVES - NO SMOKING, FLAME, OR
    WELDING WITHIN 100 FEET."
    c. Protection. Locate or barricade the powder car to protect it from
    damage. Design siding or car-passes, when used for temporary storage, to
    protect the powder car from accidental entry by other cars and to prevent
    accidental entry of the powder car to the main line. The protective devices
    installed are subject to approval of both the employer and the State entity
    having jurisdiction.
    24.6 Requirements for Handling Explosives
    24.6.1 Handling Explosives. Handle explosives carefully. Do not drop, throw,
    or slide them. Carry detonators, primers, and other explosives in separate
    containers when transporting them manually. When they are not in their original
    containers, place them in a suitable nonmetallic container for manual
    transportation.
    24.6.2 Removal from Containers. Remove explosives from their original
    containers only as needed for immediate use. Use only nonsparking tools or
    devices to open such containers. Dispose of empty containers and packing in
    accordance with the manufacturer's recommendations, or promptly burn them in
    an approved location.
    Section 24—Blasting Operations
    October 2009 24-9
    24.7 Loading Explosives and Blasting Agents
    24.7.1 Planning. Plan and schedule excavation so that drilling and loading
    operations will not conflict. Do not permit loading within 50 feet of drilling
    operations. Do not permit any activity, other than that which is required for
    loading holes, within 50 feet of loaded holes or holes that have the explosives in
    place, ready to load. A qualified blaster must supervise loading operations.
    24.7.2 Drilling. Do not drill in an area already blasted until examining
    remaining "bootlegs" (holes that do not detonate full depth) for unexploded
    charges, as well as the total area, to make sure no unexploded charges remain. Do
    not insert drills, picks, or bars into bootlegs, even if examination fails to disclose
    explosives.
    24.7.3 Loading Areas. Make boreholes ready for loading, and remove
    equipment and tools not used for loading from the area before delivering the
    explosives to the site. Isolate the loading areas with appropriate signs or
    temporary barricades to prohibit access by unauthorized people. While the bare
    holes are being loaded with explosives, exclude all personnel, other than those
    involved in the loading of boreholes, from the blast site.
    24.7.4 Boreholes. Make boreholes large enough to permit loading of cartridges
    and explosives without forcing. Prime, load, tamp, and fire as promptly as
    possible with a minimum of exposure to personnel.
    24.7.5 Tamping. Tamp only with wooden or plastic tamping poles without
    exposed metal parts. Nonsparking metal connectors on jointed poles are
    permissible. Seat cartridges by even, steady pressure, and do not tamp primers.
    24.7.6 Priming. Follow the manufacturer's recommendations in priming
    cartridges. Make primers up only at the loading area and in quantities limited to
    the number required for a single round of blasting.
    24.7.7 Stemming. Stem all blastholes in open work with noncombustible
    material to the collar or to a point that will confine the charge.
    24.7.8 Extraneous Electricity. Prohibit electric conductors, electric equipment,
    and all sources of ignition in or adjacent to the loading area. Remove lights
    50 feet from the face before starting to load in tunnels and shafts. If stray currents
    are suspected, thoroughly check out the area with suitable instruments. If stray
    currents cannot be eliminated, use nonelectrical detonators, delays, and caps.
    24.7.9 Shunts. Do not remove the manufacturer's shunt from the cap leg wires
    until you complete loading and connect the cap into the blasting circuit.
    24.7.10 Sprung Holes. Do not chamber (spring) boreholes.
    Reclamation Safety and
    Health Standards
    24-10 October 2009
    24.7.11 Blasting Mats. Where blasting may expose personnel or property to
    injury or damage from flying material, cover the charges with blasting mats.
    Carefully protect the blasting circuits, and do not permit the circuits to contact
    steel mats.
    24.7.12 Loading and Shooting. Do not leave loaded holes unattended or
    unprotected. If possible, fire all holes loaded on a shift during that same shift. If
    it is necessary to delay firing because of an emergency, isolate the area and post
    watchpersons to prevent entry to the area. Conduct aboveground blasting
    operations between sunup and sundown.
    24.7.13 Pneumatic Loading Systems. Conduct the hazards from static
    electricity and stray currents associated with pneumatically loading boreholes
    with blasting agents, take the following precautions:
    a. Use only approved pneumatic loaders.
    b. Effectively ground and bond the entire system, including placers,
    valves, and loading hose. Ground at the face in tunnels and shafts. Do not
    use piping and rails to ground the system.
    c. Following installation of the ground, check the ground with an
    approved meter to ensure that the resistance is within safe limits.
    d. Use loading hoses of an approved, nonsparking, semiconductive
    material designed to maintain static electricity within safe limits.
    24.7.14 Underground Use of Blasting Agents. Before using blasting agents
    underground, a powder technician representing the explosive manufacturer or
    supplier must inspect the proposed method of loading and the loading equipment.
    Submit written evidence of such inspection and approval of the systems.
    24.8 Wiring Operations
    24.8.1 Firing Devices. Use an electric blasting machine to fire blasts using
    electronic detonators. Do not fire blasts by connection to any other electrical
    system. Fire blasts using nonelectric detonators with a blasting machine or
    starting device prescribed by the detonator manufacturer. Do not use cap and fuse
    firing underground or in the excavation of shafts. Do not use electric blasting
    caps within 500 feet of energized high-voltage lines or facilities.
    24.8.2 Wiring Procedure. Do not remove the manufacturer's shunt from the cap
    leg wires until the cap has been connected to the leadlines or to another cap in
    preparation for the assembly of two or more caps into a single series. When firing
    two or more series of caps as a series-parallel system, make sure that the caps in
    each series are the same in number (quantity, not delay periods), and test each
    series separately with an approved blasting galvanometer to: (1) ensure that the
    Section 24—Blasting Operations
    October 2009 24-11
    series is complete, and (2) ensure that each series has the same resistance and that
    the resistance is close to the calculated resistance for the series. If the first
    reading indicates an incomplete circuit, locate the fault and correct it. If the
    second reading indicates a higher or lower resistance than calculated, correct the
    situation before final hookup and firing.
    24.8.3 Electric Caps and Delays. All caps and delays in a shot must be made by
    the same manufacturer, and the number in a circuit must not exceed the capacity
    of the blasting machine or power source.
    24.8.4 Galvanometer Testing. Make the following tests with an approved
    blasting galvanometer during all wiring operations:
    (1) Test the circuit, including all caps, before connecting it to the firing
    line.
    (2) Check the firing line before connecting it to the blasting machine or
    power source.
    24.8.5 Firing Lines. Firing lines must be of sufficient current-carrying capacity
    but not smaller than No. 14 gauge solid copper wire or equivalent. Do not
    connect the firing line to the blasting machine or power source until you have
    completed and tested the wiring and cleared the blast area. Do not ground a
    power circuit used for firing electric blasting caps.
    24.8.6 Connecting and Lead Wires. Connecting and lead wires must be
    insulated single solid wires of sufficient current-carrying capacity.
    24.8.7 Power Circuit. When using a power circuit for firing, lock the firing
    switch in the "OFF" (open) position at all times, except when firing. Design the
    power circuit so that the firing lines to the cap circuit are automatically shortcircuited
    when the switch is in the "OFF" position. Entrust the keys to the firing
    switch only to the blaster. In underground operations, the firing circuit must have
    a "lightning" gap of at least 5 feet, located between the firing switch and the
    source of power. Bridge the gap with a flexible jumper cord just before firing the
    blast.
    24.9 Firing
    24.9.1 Preparation. Before connecting the firing line to the power source, notify
    all personnel in the danger area of the blast and remove them to a safe area. Make
    satisfactory arrangements for evacuating the danger area and ensuring that no one
    enters the area before the blast.
    24.9.2 Responsibility. The blaster must be in charge of the blasting machine or
    firing switch, and must connect the firing line to the firing device. The blaster
    must make all connections from the cap circuit back to the firing device, and the
    firing line must remain shorted until connected to the firing device immediately
    before firing.
    Reclamation Safety and
    Health Standards
    24-12 October 2009
    24.9.3 Blasting Signal. Sound the following blasting signal on a clearly audible
    whistle, horn, or siren before each surface or underground blast:
    • Blasting warning: A 1-minute series of long blasts 5 minutes before
    the blast signal
    • Blast signal: A series of short blasts 1-minute before the shot
    • All clear: A prolonged blast following inspection of the blast area
    24.9.4 Posting Blasting Signals. Post blasting signals at all access points, and
    before each shot, post competent flagpersons at all access points to the danger
    area.
    24.9.5 Disconnecting. Immediately following the blast, disconnect the firing
    line from the firing power source or blasting machine and shunt it. Lock firing
    switches open.
    24.10 Inspections Following a Blast
    24.10.1 All Blasts. Before the all-clear signal, the blaster must thoroughly
    inspect to determine if all charges have fired. The blaster must carefully check
    wires and search for unexploded charges.
    24.10.2 Underground. In addition to the previously listed requirements, check
    and test the heading for adequate ventilation and safe concentrations of dusts,
    toxic vapors, and gases. Also, before permitting personnel in the heading, scale
    the face and make it safe.
    24.10.3 All-Clear Signal. Sound the all-clear signal only after satisfactorily
    completing the inspection.
    24.11 Requirements Regarding Misfires
    If you suspect or find a misfire, keep all personnel, except the blaster and
    employees necessary to handle the misfire, out of the danger area. Prohibit all
    work in the danger area except that necessary to remove the misfire hazard. If a
    misfire occurs while using cap and fuse, all personnel must remain at a safe
    distance from the charge for at least 1 hour. If other electric or nonelectric
    initiating methods are used, the blasting supervisor may reduce the waiting period
    to 30 minutes.
    24.11.1 Refiring. Refiring is the desired method of clearing misfires. The
    following actions are mandatory:
    a. For electrically fired blasts in which broken wires or faulty connections
    caused the misfire, make repairs, reconnect the firing line, and attempt to
    fire the charge.
    b. For misfires originally initiated by detonating cord or nonelectrical
    detonators, the blaster must inspect lines coming out of the holes, and if
    Section 24—Blasting Operations
    October 2009 24-13
    they appear to be intact, the blaster can reconnect them and attempt to
    detonate the misfired holes.
    c. In blastholes where leg wires are discontinuous or leads or detonating
    cord cut off, there may still be explosives in the hole that can be reprimed
    and fired. Remove any stemming in the hole. Float stemming out with
    water. Place a new primer in the hole and attempt to fire the charge.
    24.11.2 Removal of Explosives. This procedure must be the last resort. Perform
    it only when refiring has failed or when refiring would present a hazard. Remove
    explosives by washing them out with water, or, if the misfire is underwater, blow
    them out with air.
    24.11.3 Work Restrictions. Do not permit drilling, digging, or picking until:
    (1) you have detonated all missed holes or removed the explosive, and (2) the
    blaster has approved the resumption of work.
    24.12 Requirements for Using Safety Fuses
    Use safety fuses only where sources of extraneous electricity make the use of
    electric caps dangerous. Do not use damaged fuse or fuse with sharp kinks.
    24.12.1 Capping. Before capping a safety fuse, cut a short length from the end
    to ensure a fresh-cut end in each blasting cap.
    24.12.3 Crimper. Use cap crimpers of approved design for attaching blasting
    caps to safety fuse.
    24.12.4 Length of Fuse. The minimum length of safety fuse must be as required
    by State law, but it must not be less than 30 inches. Provide the blaster sufficient
    time to permit the blaster to reach a place of safety.
    24.12.5 Multiple Cap and Fuse Use. At least two blasters must be present when
    multiple cap fuse blasting is done by hand lighting methods. Each blaster must
    light no more than 12 fuses when using hand-lighting devices.
    24.12.6 Mudcapping. Do not use cap and fuse to fire mudcap charges unless
    you separate the charges sufficiently to prevent one charge from dislodging other
    shots in the blast.
    24.13 Use of Detonating Cord
    24.13.1 Care in Use. Use only detonating cord consistent with the type and
    physical condition of the borehole, stemming, and the type of explosive.
    Consider and handle detonating cord in the same manner as other explosives.
    Reclamation Safety and
    Health Standards
    24-14 October 2009
    24.13.2 Installation. Cut the line of detonating cord extending out of a borehole
    or from a charge from the supply spool before loading the remainder of the hole
    or placing additional charges. All runs must be free of loops, sharp kinks, or
    angles that take the cord back toward the oncoming line of detonation.
    24.13.3 Connections. Detonating cord connections must be competent and
    positive and in accordance with approved and recommended methods. Make
    knot-type or other cord-to-cord connections only with detonating cord in which
    the explosive core is dry. Inspect connections before firing.
    24.13.4 Use of Delays. When using detonating cord millisecond-delay
    connectors or short-interval-delay electric blasting caps with detonating cord,
    follow the manufacturer's recommendations.
    24.13.5 Connecting Blasting Caps. When connecting blasting caps to
    detonating cord, tape or otherwise attach the cap securely along the side or the
    end of the cord, with the end of the cap containing the explosive pointed in the
    direction in which the detonation is to proceed.
    24.13.6 Detonators. Do not bring detonators for firing the trunkline to the
    loading area, and do not attach the detonating cord until everything else is in
    readiness for the blast.
    24.14 Underwater Blasting
    24.14.1 Supervision. A competent blaster must conduct all blasting operations.
    Do not fire any blast without that person’s approval.
    24.14.2 Loading Tubes. Do not use loading tubes and casings of dissimilar
    metals for electric or other stray-current-affected detonators or explosives. When
    tubes are necessary, load these electrically affected devices through nonsparking
    loading tubes.
    24.14.3 Detonators. For underwater blasting operations, use only water-resistant
    blasting caps and detonating cord or other detonators and/or firing systems and
    methods approved by the manufacturer.
    24.14.4 Marking Charges. When placing more than one charge underwater,
    attach a float device to an element of each charge so that it will be released by the
    firing. Handle misfires using precautions and procedures in this section.
    24.14.5 Blast Warning. In addition to the standard audible blast warning,
    display blasting flags.
    24.14.6 Boats in Area. Do not fire blasts while any vessel underway is within
    1,500 feet of the blasting area. Notify those onboard vessels moored or anchored
    within 1,500 feet before the blast is fired.
    Section 24—Blasting Operations
    October 2009 24-15
    24.14.7 Swimming and Diving. Do not fire blasts when swimmers or divers are
    in the vicinity and exposed to injury from the blast.

  2. 2 کاربر از پست مفید ابوالحسنی محمد سپاس کرده اند .


اطلاعات موضوع

کاربرانی که در حال مشاهده این موضوع هستند

در حال حاضر 1 کاربر در حال مشاهده این موضوع است. (0 کاربران و 1 مهمان ها)

موضوعات مشابه

  1. Machining Technology: Machine Tools and Operations
    توسط ریپورتر در انجمن سامانه های انرژی و قدرت
    پاسخ ها: 0
    آخرين نوشته: 20th May 2009, 11:44 AM

کلمات کلیدی این موضوع

مجوز های ارسال و ویرایش

  • شما نمیتوانید موضوع جدیدی ارسال کنید
  • شما امکان ارسال پاسخ را ندارید
  • شما نمیتوانید فایل پیوست کنید.
  • شما نمیتوانید پست های خود را ویرایش کنید
  •